We are having a problem with the loss of modbus communications between ABB protection relays and our ControLogix PLC.
We have several (approx 25) 11kV and 3.3kV switchboards comprising ABB protection relays (approx 120 x REF610, 15 x RET541, 15 x REX521). The relays communicate via Modbus RTU to a Prosoft Modbus card (MVI56-MCM) located in Allen Bradley ControLogix Racks. There is no more than 8 relays on an segment so multiple relays, Prosoft cards and ControLogix Racks are involved.
Communications is stable to all nodes for an extended period (days) and then one relay will not respond. The failed relay is random and does not appear to be coincident with large motor starts or other electrical noise. Response is identified by looking at the receive packet counter in RSLogix for the failed node and recognising that it does not increment. The master continues polling adjacenet nodes successfully. Power cycling the failed relay reestablishes communications to the relay.
Cable segments are Unitronic Comms cables with a characteristic impedance of 100-120 Ohms.
Has anyone had similar problems with the ABB relays on Modbus? What can I do to be 100% sure it is the relays that are the problem?
Chris Devine
We have several (approx 25) 11kV and 3.3kV switchboards comprising ABB protection relays (approx 120 x REF610, 15 x RET541, 15 x REX521). The relays communicate via Modbus RTU to a Prosoft Modbus card (MVI56-MCM) located in Allen Bradley ControLogix Racks. There is no more than 8 relays on an segment so multiple relays, Prosoft cards and ControLogix Racks are involved.
Communications is stable to all nodes for an extended period (days) and then one relay will not respond. The failed relay is random and does not appear to be coincident with large motor starts or other electrical noise. Response is identified by looking at the receive packet counter in RSLogix for the failed node and recognising that it does not increment. The master continues polling adjacenet nodes successfully. Power cycling the failed relay reestablishes communications to the relay.
Cable segments are Unitronic Comms cables with a characteristic impedance of 100-120 Ohms.
Has anyone had similar problems with the ABB relays on Modbus? What can I do to be 100% sure it is the relays that are the problem?
Chris Devine