jdenison
Electrical
- Aug 27, 2009
- 4
we have had 2 large 480 motor w/ soft starts installed both seem to be failng on start up they both are 164 amp. we have an adjust. trip setting breaker ahead of a soft start set at approx 900+ amp for inrush which you would think should be plenty. I see no faults in history of soft start and everything looks good physically load side fo soft start but it keeps tripping the breaker. We have on one motor a high winding temp on C PHASE and a high inboard bearing temp. We saw the fault of no load on C, but we did get the motor restarted it ran for quite some time and went back out on high winding temp. Is the inrush setting sufficent? What may cause this high winding temp if the motor megs out fine? we are running this motor at 95% to 100% which should be a happy point. C phase is approx 15 degrees higher than A or B according to our SCADA system.