saladhawks
Electrical
- Jun 4, 2004
- 86
The electric utility I work for recently experienced a 4 kV Overhead Distribution Circuit line down, where all 3 phases of 4 kV circuit burned clear mid span. Span where 4 kV circuit burned clear had double-ended construction on both sides, so there was no significant tension on this span. All 3 phases of 4 kV circuit that burned clear were 336 All Aluminum Conductor (AAC) with low voltage tree insulation.
Initiating event was a 34 kV over-build circuit dropping a single phase bare conductor onto this 4 kV under-built circuit. 4 kV circuit went through a series of reclose shots and then subsequently held with normal load current of approximately 50 Amperes per phase for 60 seconds.
After 60 seconds, 4 kV circuit relayed out and reclosed again. Circuit held, but load current was now 0 Amperes. Circuit was then cleared from SCADA due to closed circuit breaker with no current indicating an energized line down condition.
Most interestingly, the distance between initiating 34 kV circuit event and where under-built 4 kV circuit phase conductors burned clear is approximately 1,000 feet apart, separated by multiple pole spans.
I am having trouble grasping how it would be possible to burn clear 336 AAC conductors that far away from initiating event.
Any thoughts would be greatly appreciated.
Initiating event was a 34 kV over-build circuit dropping a single phase bare conductor onto this 4 kV under-built circuit. 4 kV circuit went through a series of reclose shots and then subsequently held with normal load current of approximately 50 Amperes per phase for 60 seconds.
After 60 seconds, 4 kV circuit relayed out and reclosed again. Circuit held, but load current was now 0 Amperes. Circuit was then cleared from SCADA due to closed circuit breaker with no current indicating an energized line down condition.
Most interestingly, the distance between initiating 34 kV circuit event and where under-built 4 kV circuit phase conductors burned clear is approximately 1,000 feet apart, separated by multiple pole spans.
I am having trouble grasping how it would be possible to burn clear 336 AAC conductors that far away from initiating event.
Any thoughts would be greatly appreciated.