jimmy2times
Electrical
- Jun 26, 2007
- 138
Im familiar with issues of 2speed motor and changing from high to low speed. But is also changing from low to high speed also problematic?
Fan starter has recently had impeller change (blade change and material change)but now protection trips on switch from low to high speed. Not sure if issues existed previously. Now some starts ok but others trip on high speed instantaneously.
Upped instantaneous as a temp arrangement to allow fan to run. Motor running current in high speed is below rated.
Put analyser on current and sees x15 inrush where motor nameplate says 7 x flc.
Could this be similar issue to open transition starter problem issues when motor briefly open circuit? I read a post referring to Westinghouse advice to include timer to allow magnetic flux to decay (1-2 secs) we don’t have this presently