Hi guys, I have a project in a building constructed in 1930. The Owner wants to convert the mezzanine into public assembly usage. Original use was office space. The original drawings describe the floor joists as 10" J 8c L's @ 8.96. Right now access is non-existent due to a plaster hard lid ceiling. Before I direct the contractor to do some selective demo the owner would like to know more info. Anybody have or know where to find info on these joists?
 
Replies continue below

Recommended for you

Thanks anyway SlideRule.....Jones & Laughlin was bought out in the 60's (I think) and since then a succesion of companies ending with Arcelor Mittal have swallowed each other. J&L historical info seems to have been long lost. Since they are hard to read I may have misread the old plans. It may be "J Bc L's." I think they are an early proprietary bar joist. SJI first published a Standard Specification in 1928 but not every manufacturer joined up.
 
nutte - that is fantastic.

You might scan the whole section (if there's more) and send it over to SlideRuleEra for his website.

 
A star for SlideRule as well. He had the knowledge of those beams. I just had the book.
 
You guys are fantastic. Thanks. I have AISC's Design Guide 15 and it wasn't anywhere in there.
 