acog
Electrical
- Jul 30, 2010
- 31
I am performing some basic pre-commissioning tests on a 132kV transmission line shortly. The line is around 40km in length and is earthed at both ends with portable earths. Several medium voltage and high voltage lines run parallel or intersect this transmission line over the route.
I am concerned about induction on the line during testing (particularly when the earths are removed). Is there a method to check the extent of induced voltage on the line prior to connecting a test instrument?
Note: no voltage transformers are connected to the line.
I am guessing I could use a clamp style ammeter (also known as 'tong') or a rogowski coil to measure the current flowing through the portable earth prior to removal. The measured current may give me an indication of the prospective induced voltage on the phase conductor after portable earth removal.
Is there an 'industry best practice' procedure to do test for induction?
Also, I am using a typical Megger 5kV insulation tester for the insulation resistance and continuity tests. I am simply going to lift the earths off one phase, perform a 1 minute test at 5kV on the isolated phase to the other phases and ground to confirm insulation resistance.
Then for confirmation of continuity, I plan to install an earth at the remote end on the phase under test and test again which should give me a low resistance (voltage collapse). Is this the industry standard procedure?
Appreciate your comments/thoughts.
I am concerned about induction on the line during testing (particularly when the earths are removed). Is there a method to check the extent of induced voltage on the line prior to connecting a test instrument?
Note: no voltage transformers are connected to the line.
I am guessing I could use a clamp style ammeter (also known as 'tong') or a rogowski coil to measure the current flowing through the portable earth prior to removal. The measured current may give me an indication of the prospective induced voltage on the phase conductor after portable earth removal.
Is there an 'industry best practice' procedure to do test for induction?
Also, I am using a typical Megger 5kV insulation tester for the insulation resistance and continuity tests. I am simply going to lift the earths off one phase, perform a 1 minute test at 5kV on the isolated phase to the other phases and ground to confirm insulation resistance.
Then for confirmation of continuity, I plan to install an earth at the remote end on the phase under test and test again which should give me a low resistance (voltage collapse). Is this the industry standard procedure?
Appreciate your comments/thoughts.