Does anyone see any issues with this detail?
TIA
Pretty sure you're saying a W10x15 is 8 1/8" tall, and I like steel to create torsional stability in the beam (usually an end plate).
Oops. My bad. It's a W8x15.
I can put a pair of stiffeners near the end of the beam., but won't the nailer attached to the floor sheathing provide torsional resistance?
Thank you for your response.
I question the ability of the 2 or 3 10dx1-1/2" nails near the end of the beam to meet the requirements of AISC J10.7. But you have the whole picture - if you can conclude that it does the job, then great.
Normally, I bear the steel beam directly on the PSL post, but I see no issue with your detail, especially considering the relatively light load of only 4k. Rather than use a pair of stiffeners, I'd have a 1/4" plate welded to the end of the beam.
The end plate is cheap. I would specify it regardless.
I would also prefer to connect directly to the post, but I agree for light loads it probably doesn't make much difference.
For me, I would have no attachment to the post and use studs instead of PSL for only 4K. The floor diaphragm will keep it in place.