i AM TRYING TO DESIGN A SIMPLE SHEAR PLATE USING RAM CONNECTION, AND WEHN I WAS LOOKING AT THE REPORT I COUDNT FIGYRE IUT HOW DID THE SOFTWARE CALCULATE THE VALUE OF THE WELD COEFFICIENT, WHEN I DID THE CALCULATION MANUALLY IT GAVE ME A DIFFERENT VALUE:

HERE IS HOW THE SOFTWARE CALCUATAES THE WELD STRENGTH:

Verification Unit Capacity Demand Ctrl EQ Ratio References


Weld capacity [KN] 219.42 50.00 1V - DL 0.23 Tables 8-4 .. 8-11

fRn = f*C*C1*D*L = 0.75*0.650122[KN/mm]*1*3*150[mm] = 219.42[KN] Tables 8-4 .. 8-11

#AND ATTACHED IS THE DIMENSION OF THE CONNECTION

 
 http://files.engineering.com/getfile.aspx?folder=a4403d7c-7e80-4df8-a416-07f53e7d83b5&file=shear.png