Weep Holes on PSV Discharge 1

Status
Not open for further replies.

RJB32482

Chemical
Jan 19, 2005
271
What situations is a weep hole needed on the discharge of PSV's? I could not find it it APT 520 Part 2.

Thanks
 
Replies continue below

Recommended for you

Condensation (dew), rain, sleet, snow, cleaning activities by contractors that don't know better, etc. Especially if the discharge has a vertical run where accumulated liquid can appreciably affect the opening pressure due to backpressure.

Good luck,
Latexman
 
RJB32482,

In addition to Latexman's comments and for a reference in API RP-520 Part II, look at Figure 1, Typical Pressure Relief Valve Installation: Atmospheric (Open) Discharge. Note 2 references a weep hole.
 
Ok just looked in text and not in the figures. Thank you both for the excellent learning infrmation.
 
You are most welcome! Since you are new, you can thank folks for a valuable post by giving them a star. Click the left link under each post you are thankful for.

Please don't give me a start now. I don't want folks to think I'm begging. Thanks!

Good luck,
Latexman
 