Hi Fellows
I designed a web side plate connection which 2 columns, 3 rows M20 bolt to the 250UB25.7, and 10E48SP CFW to the web of 410UB59.7. My plate size is 210x180x8. Calculate by hand follow the AISC (design of Structural connections, everything is satisfactory. But I put it in to the Limcon, it shows the error because the distance between the first row of bolt from top to the top of the flange shall be (70-100mm). But this is no this requirement in the book. Shall I follow this requirement? and if there is enough spaces for the 250UB25.7 rotate and create a flexible connection, shall I still need to meet this geometry requirement?
Thank you for your time.
I designed a web side plate connection which 2 columns, 3 rows M20 bolt to the 250UB25.7, and 10E48SP CFW to the web of 410UB59.7. My plate size is 210x180x8. Calculate by hand follow the AISC (design of Structural connections, everything is satisfactory. But I put it in to the Limcon, it shows the error because the distance between the first row of bolt from top to the top of the flange shall be (70-100mm). But this is no this requirement in the book. Shall I follow this requirement? and if there is enough spaces for the 250UB25.7 rotate and create a flexible connection, shall I still need to meet this geometry requirement?