VSD and short circuit contribution 1

Status
Not open for further replies.

Murlinor

Electrical
Apr 12, 2008
24
Hello friends.

I have a 6.6 kV VSD connected to a 6.6/50 kV transformer. I am designing a 50 kV switchgear panel and was wondering if the VSD will contribute to the short circuit current at the 50 kV busbar?

Thanks
 
Replies continue below

Recommended for you

It depends on the drive. If it is a regenerative-type, then yes there will be some limited fault contribution. If it is non-regenerative, then no.

David Castor
 
Generally speaking, the VSD contribution to the upstream short circuit current is limited to the VSD current overload capability.
 