Hello guys,
i have to connect a generator of 1125 KVA of 400 V line to line 50 Hz frequency with an Automatic Transfer switch.
the ATS is located 15 meters away from the generator, the company that made the conception of the project implies that we have to use a cable of 12 x (1x300 ) + 4x (1x150) + 4x(1xG150).
the problem is that i have only three terminals on the generator's circuit breaker wich means i can only use three cable for each phase ( 900 mm2 cable section instead of 1200 mm2 )
- the whole power consumption is 869.1 Kw.
- how can i calculate the voltage drop in case of using only 9x(1x300 mm2 ) instead of 12x (1x300 mm2).
thank you in advance.