VFD setup without load attached

Status
Not open for further replies.

devittjl

Electrical
Apr 4, 2002
7
Can I power up vfd without a load attached?

I need to verify paramters/set drive parameters to a panel I recieved but to not have the motors to attach as a load.

thanks
 
Replies continue below

Recommended for you

Yes, but features like auto-tune for vector drives will not work. You'll have to enter the motor parameters manually if you have them, or you're limited to a V/Hz mode of operation.


----------------------------------