controlnovice
Electrical
- Jul 28, 2004
- 976
Have a 480Vac, 200HP well pump (motor and pump in well) driven by VFD.
Distance between VFD and motor is 1300 ft using buried armoured cable. Sorry, don't have cable size yet.
We have a bypass contactor around the drive, and the motor/pump starts and runs without problem using it.
Original cable was same, armoured cable, but a larger size (again, don't have sizes yet), and the VFD ran the motor without issues (or without tripping). BUT, we did recently get a ground fault on the cable and had to change it. We happen to have the smaller cable (again, no size yet) running/installed parallel with the larger one (for a previously smaller well pump/motor) that we found was large enough for the larger motor. So we used it instead of installing a new cable.
We do have reactor on load side of VFD.
Ever since using the smaller cable, we've been experiencing high DC bus voltage on the VFD on start.
Any ideas why it would work on larger cable, and not smaller cable, even though smaller cable is sized for the amp load?
Length of cable vs size of cable?
Armoured cable creating choke?
Length of cable creating larger reflective wave?
______________________________________________________________________________
This is normally the space where people post something insightful.
Distance between VFD and motor is 1300 ft using buried armoured cable. Sorry, don't have cable size yet.
We have a bypass contactor around the drive, and the motor/pump starts and runs without problem using it.
Original cable was same, armoured cable, but a larger size (again, don't have sizes yet), and the VFD ran the motor without issues (or without tripping). BUT, we did recently get a ground fault on the cable and had to change it. We happen to have the smaller cable (again, no size yet) running/installed parallel with the larger one (for a previously smaller well pump/motor) that we found was large enough for the larger motor. So we used it instead of installing a new cable.
We do have reactor on load side of VFD.
Ever since using the smaller cable, we've been experiencing high DC bus voltage on the VFD on start.
Any ideas why it would work on larger cable, and not smaller cable, even though smaller cable is sized for the amp load?
Length of cable vs size of cable?
Armoured cable creating choke?
Length of cable creating larger reflective wave?