- Sep 12, 2005
- 5,375
I'm looking at a power factor correction case and the utility meter almost never reads above 0.707. There are a few measurements higher but most are either 0.707 or they are lower. The loads are all inductive yet the addition of power factor capacitors has caused the kVAR to appear higher and the power factor to appear lower compared to the metering data from before the capacitor bank addition.
The meter readings are from the meter's 15 minute fixed window demand calculations where it will give kVA, kVAR, kW and power factor for each 15 minute period. Is there anything odd the meter might be doing while calculating these demand values?
When using a power logger on site with the equipment running, the average power factor never goes below 0.9 lagging. The power factor curve recorded every second is actually quite flat varying between about 0.92 and 0.94 during the 1/2 hour I was monitoring.
Yet, utility meter data from other days with the equipment running always show a poor power factor never above 0.7 (it's not clear if this is leading or lagging).
Does anyone else believe the meter must simply be connected wrong?
If it's not a connection issue, then what could be the problem?
The meter readings are from the meter's 15 minute fixed window demand calculations where it will give kVA, kVAR, kW and power factor for each 15 minute period. Is there anything odd the meter might be doing while calculating these demand values?
When using a power logger on site with the equipment running, the average power factor never goes below 0.9 lagging. The power factor curve recorded every second is actually quite flat varying between about 0.92 and 0.94 during the 1/2 hour I was monitoring.
Yet, utility meter data from other days with the equipment running always show a poor power factor never above 0.7 (it's not clear if this is leading or lagging).
Does anyone else believe the meter must simply be connected wrong?
If it's not a connection issue, then what could be the problem?