acog
Electrical
- Jul 30, 2010
- 31
I have a problem with a new substation which is fed from an unrestricted 11kV feed. The substation upstream has an 11kV fault level of approx 7kA and is located 200m away.
I want to reduce the fault current so that the touch voltages within the new substation comply with IEC/AS standards.
Currently the plan is to install an 11kV/11kV isolation transformer (Dyn) with an earthing resistor on the neutral.
However, a fault (for example) from the incoming side (delta) of the isolation transformer to the tank will bypass the earthing resistor, and put a full 7kA fault to the ground grid again.
To solve this I have suggested moving the isolation transformer to a remote location and restricting access. This is problematic due to space contraints and high EPR.
Is there a better way we can pull the fault current down?
Are my assumptions correct on the earthing transformer?
I want to reduce the fault current so that the touch voltages within the new substation comply with IEC/AS standards.
Currently the plan is to install an 11kV/11kV isolation transformer (Dyn) with an earthing resistor on the neutral.
However, a fault (for example) from the incoming side (delta) of the isolation transformer to the tank will bypass the earthing resistor, and put a full 7kA fault to the ground grid again.
To solve this I have suggested moving the isolation transformer to a remote location and restricting access. This is problematic due to space contraints and high EPR.
Is there a better way we can pull the fault current down?
Are my assumptions correct on the earthing transformer?