Transformer inrush current - 2

Status
Not open for further replies.

cherry2000

Electrical
Jun 21, 2007
99
Once more on the same topic..I could locate some literature for calculating the worst 1st cycle inrush, based on the Transformer parameters like flux density, dimensions etc.See attached.

Next, I tried my hand at calculating the reduction in inrush because of line reactance. The reduction was not as much as desired. 1540Amps reduced to 1340Amps approx for a 150kVA, 3Ph, Dy Transformer. The power supply cable was 4/0, 200m. Does anybody have any idea on the transient analysis program for carrying out a study?

It is my belief that accounting for source impedance & cable resistance will further lower the inrush value.
 
Replies continue below

Recommended for you

It is my belief that accounting for source impedance & cable resistance will further lower the inrush value.

Is someone disagreeing with you on this? The S&C white paper referenced in previous thread (I think) confirms this. The cable impedance effectively increases the source impedance.

 
I am looking for a rigorous calculation to get the final value. Thanks for the support.
 
There is no final value. The inrush depends on voltage phase angle at energization as well as remanence flux. You can estimate a maximum worst-case value, or get it from the transformer supplier.

Perhaps a transient program such as ATP can help - it may have already been modeled at some point, but you'll need a lot of specific data on the particular transformer of interest. And make quite a few assumptions.

 
cherry2000
For what you need a final value?
Take a worst case,as Dave recommended.
Best Regards.
Slava
 