A client wants to put in a new opening in an existing solid concrete tilt-up wall that is in the order of 16 feet wide (quite long in my opinion and I will push for less).
That being said, X-ray scans show #7 verticals at an average of 17" on center with #5 horizontals. There is 3" of cover on the #7 bars.
This seems like a lot of reinforcing to me for a 22 foot high, 6" thick panel. I have never used over #5 bars for a panel of this thickness and height, going to two layers of reinforcing at short panel legs where necessary to limit the bar size. These bars appear to be placed in a single layer at the center of the panel.
Has anyone constructed panels in this manner using larger rebar? If so, was there any reason to go with larger bars in the center rather than two layers - and I would not expect to have to use two layers of bars in a solid panel. I would expect #4 or #5 @14 to 15" OC in the center of the panel.
Current As = .6/1.43 = .42 in sq./ft. => #5 @ 8" OC for smaller bars in the center. Panel seems over-reinforced to me. Lifting would not have changed the reinforcing that much... Shear? Seems to be plenty of wall though.
Am I missing something here?
Mike McCann, PE, SE (WA, HI)
That being said, X-ray scans show #7 verticals at an average of 17" on center with #5 horizontals. There is 3" of cover on the #7 bars.
This seems like a lot of reinforcing to me for a 22 foot high, 6" thick panel. I have never used over #5 bars for a panel of this thickness and height, going to two layers of reinforcing at short panel legs where necessary to limit the bar size. These bars appear to be placed in a single layer at the center of the panel.
Has anyone constructed panels in this manner using larger rebar? If so, was there any reason to go with larger bars in the center rather than two layers - and I would not expect to have to use two layers of bars in a solid panel. I would expect #4 or #5 @14 to 15" OC in the center of the panel.
Current As = .6/1.43 = .42 in sq./ft. => #5 @ 8" OC for smaller bars in the center. Panel seems over-reinforced to me. Lifting would not have changed the reinforcing that much... Shear? Seems to be plenty of wall though.
Am I missing something here?