Hey guys,
A little help in here.
I have read in a literature from spirax sarco that the conductivity of boiler water is dependent upon its temperature. I was so struck by this statement because our current practice for measuring the TDS of the boiler water is to get the sample from the boiler and let it cool down in an enclosed bottle. After the temperature has cooled down to its ambient temperature, we measure its conductivity. To convert conductivity into TDS of water, we just multiply it by 0.7 (TDS = 0.7 x conductivity).
If we follow a statement from spirax sarco literature, it seems that we are doing a very inaccurate measurement of the true value of the TDS inside the boiler. We are actually understated the TDS of the boiler.
Any suggestions regarding this?
A little help in here.
I have read in a literature from spirax sarco that the conductivity of boiler water is dependent upon its temperature. I was so struck by this statement because our current practice for measuring the TDS of the boiler water is to get the sample from the boiler and let it cool down in an enclosed bottle. After the temperature has cooled down to its ambient temperature, we measure its conductivity. To convert conductivity into TDS of water, we just multiply it by 0.7 (TDS = 0.7 x conductivity).