prc
Electrical
- Aug 18, 2001
- 2,013
In my country Generator transformers are provided with DETC (de-energized Tap-changers). In case of transformers for thermal sets (50-800 MW) tap-changers with +- 10 % tap range(9 tap) were used to be there. Later this range was reduced to 5 tap with +- 5 % range as these tap-changers are never used once the unit is commissioned. From transformer manufacturer's angle, it is better to reduce the tap range and if possible eliminate it altogether for higher reliability. I understand in UK and Germany, GSUs are provided with OLTC with wide tap range. My understanding is they use high impedance transformers and reactive power control is done by operation of OLTC. When DETC is used, reactive power control is by adjusting the AVR of generator.
In Hydro power stations, our major utility eliminated DETC and now procuring GSU without tap-changer. Is there a difference in reactive power contribution by thermal and hydro sets? What is the practice in other parts of the world? My point is if an accessory is never used in its life time, why it should be provided in the first instance itself? Requesting guidance from operating engineers in the field.
In Hydro power stations, our major utility eliminated DETC and now procuring GSU without tap-changer. Is there a difference in reactive power contribution by thermal and hydro sets? What is the practice in other parts of the world? My point is if an accessory is never used in its life time, why it should be provided in the first instance itself? Requesting guidance from operating engineers in the field.