UtilityGy
Electrical
- Mar 5, 2010
- 35
Hello All,
I am buying a 4.16 KV swgr fed by two incoming XFRM's rated 5 MVA, 27.6 kV/4.16 kV. Both will operate in parallel with no tie.
Voltage= 4.16 kV
TR1= 5 MVA %Z1= 5
TR2= 5 MVA %Z2=5
Short Circuit Contribution MVA(TR1)= 20 P.U.=13895 A
Short Circuit Contribution MVA(TR2)= 20 P.U.=13895 A
Total Contribution= 40 P.U.
S.C Contribution(Total from TR1 & TR2)= 27790 A
My switchgear is rated at 31.5 kVA rms symettrical. I just wanted a second opinion if I am missing anything in calculating maximum short circuit contribution towards 4.16 kV switchgear.
....
Appreciate your input !