- Aug 15, 2002
- 230
480V, 3Ph, Paralleling SWBD rated at 100kAIC.
Using SKM the 3 phase bolted fault calculated at 91.8kA with x/r=15.4
L-G fault calculated at 121.8 with x/r=12
Does a normal 3 phase switchboard short circuit rating of 100kA have any associated L-G rating, or do I use the 3 phase rating?
Does this SWBD fail a short circuit evaluation?
I realize the breakers need to have a multiplier since the x/r is higher than the test value, but I'm trying to focus on the SWBD first.
Thanks