Surge arrestor and EPR 1

Status
Not open for further replies.

kaspor

Electrical
Aug 12, 2021
52
Hello

I am trying to understand the inner workings of surge arrestors. If a surge arrestor diverts current to ground once line voltage is above a certain threshold, does that mean you will get an earth potential rise at the surge arrestor output? For example, if I measured the voltage between the end of the surge arrestor and transformer STAR point (i.e. remote earth), would there be a voltage present?

Or does it somehow absorb the over voltage?

 
Replies continue below

Recommended for you

You would read a voltage equal to the current times the impedance of the path from the arrestor to the transformer neutral.

--------------------
Ohm's law