After only 2 years a leak occurred on a 3/4" seamless carbon pipe (schedule 40) carrying ammonia liquid and gas.
The pipe is insulated with pre-moulded pu and the cladding are with plastic tape. The pipe wills every 4 hours be cold (-25 dg C/-13 dg F) for approx 3 min, chilled (5 dg C/42 dg F) for 20 min and hot (50 dg C/120 dg F) for 2 min.
The pipe was not surface treaded before it was insulated and no damage of the insulation was found.
The pipe is on the sealing in a food processing plant and the roof space is normally good ventilated.
There is many other refrigeration pipes in same space with same conditions but only with constant temperature ranging from (-25 dg C/-13 dg F) to (5 dg C/42 dg F), those pipes have no corrosion.
I have a feeling that the temperature is the main reason and this is due to the insulation is not moisture tight enough since the leaks occurs where the pre-moulded insulation is joining and the rest of the pipe has a high but constant surface corrosion.
My intention is to change the pipe to a schedule 80 and then use a good insulation.
Any comments or experience will be very welcome.
The pipe is insulated with pre-moulded pu and the cladding are with plastic tape. The pipe wills every 4 hours be cold (-25 dg C/-13 dg F) for approx 3 min, chilled (5 dg C/42 dg F) for 20 min and hot (50 dg C/120 dg F) for 2 min.
The pipe was not surface treaded before it was insulated and no damage of the insulation was found.
The pipe is on the sealing in a food processing plant and the roof space is normally good ventilated.
There is many other refrigeration pipes in same space with same conditions but only with constant temperature ranging from (-25 dg C/-13 dg F) to (5 dg C/42 dg F), those pipes have no corrosion.
I have a feeling that the temperature is the main reason and this is due to the insulation is not moisture tight enough since the leaks occurs where the pre-moulded insulation is joining and the rest of the pipe has a high but constant surface corrosion.
My intention is to change the pipe to a schedule 80 and then use a good insulation.
Any comments or experience will be very welcome.