IEEE80(2000) has Sf current split factors shown on page 153 for a Dist gnd of 25 ohms vs one for 200 ohms. The table on page 151 line 4 from the bottom says R=.322 and X=.242 for 25 ohms and then R=1.65 and X=.291 for 200 ohms (the far right column heading is wrong and should say Rdg=200).
If I am at 30 ohms for my Dist gnd, am I forced to use the R=1.65/X=.291 and not the R=.322/X=.242 because I am over 25 ohms? Can I interpolate a value for my 30 ohm actual condition? If so, how?
At R=.322/X=.242, I easily pass my Touch and Step potentials, but at R=1.65/X=.291 I have a hard time passing as the R value is five times larger. I just barely missed the 25 ohm limit at 30 ohms and want to know if there is a way to prorate the R and X values for a Dist gnd of 30 ohms.
If I am at 30 ohms for my Dist gnd, am I forced to use the R=1.65/X=.291 and not the R=.322/X=.242 because I am over 25 ohms? Can I interpolate a value for my 30 ohm actual condition? If so, how?
At R=.322/X=.242, I easily pass my Touch and Step potentials, but at R=1.65/X=.291 I have a hard time passing as the R value is five times larger. I just barely missed the 25 ohm limit at 30 ohms and want to know if there is a way to prorate the R and X values for a Dist gnd of 30 ohms.