So say you have a five story hotel, made out of wood.
The stairs are completely enclosed. typical set up
1. is sprinkler protection required at the intermediate landings?
2. or is it the intention of the one at the top to protect the intermediate, depending on the layout.
3. 8.15.3 uses the word "beneath" is that for totally open stairs, as in no walls?
4. I know appendix is not, but seems like a conflict between 8.15.3.1.2* and A.8.15.3.1.2.
8.15.3 Stairways.
8.15.3.1 Combustible Construction. Sprinklers shall be installed beneath all stairways of combustible construction.
8.15.3.1.1 Sprinklers shall be installed at the top of combustible stair shafts.
8.15.3.1.2* Sprinklers shall be installed under the landings at each floor level.
A.8.15.3.1.2 Sprinklers at each floor level landing should be positioned to protect both the floor level landing and any intermediate landing.
8.15.3.1.3 Sprinklers shall be installed beneath the lowest intermediate landing.
Thank you
The stairs are completely enclosed. typical set up
1. is sprinkler protection required at the intermediate landings?
2. or is it the intention of the one at the top to protect the intermediate, depending on the layout.
3. 8.15.3 uses the word "beneath" is that for totally open stairs, as in no walls?
4. I know appendix is not, but seems like a conflict between 8.15.3.1.2* and A.8.15.3.1.2.
8.15.3 Stairways.
8.15.3.1 Combustible Construction. Sprinklers shall be installed beneath all stairways of combustible construction.
8.15.3.1.1 Sprinklers shall be installed at the top of combustible stair shafts.
8.15.3.1.2* Sprinklers shall be installed under the landings at each floor level.
A.8.15.3.1.2 Sprinklers at each floor level landing should be positioned to protect both the floor level landing and any intermediate landing.
8.15.3.1.3 Sprinklers shall be installed beneath the lowest intermediate landing.
Thank you