WAstruc10
Structural
- Nov 27, 2002
- 45
I have a fixed pier in a high seismic zone, for which the geotech has specified 16" square prestressed piles. For the spiral reinforcing, I need 2" cover (marine environment) so I am left with a core diameter (Dc) of 12". Works fine with equation 21-2 (ps=0.12f'c/fyt), which calculates to #3 spiral at 3" pitch. But then ACI states "shall not be less than req'd by eq. 10-5"...and that equation seems to give huge unrealistic values for the spiral reinforcing - #5 spiral at 1.81" pitch! Seems like this is the case due to the ratio of Ag to Ach being much larger than it would be with square ties in a square column, but 16" square piles with spiral cage are very common, no? Am I missing something, or does anyone know how this is commonly handled? Much thanks...