chileheadcraig
Civil/Environmental
- Nov 15, 2002
- 50
We have a maximum velocity limit of 10 ft/s used as guidance for sizing water mains in our system, which includes fire flows. It seems that when this topic is discussed, its with regard to the design fire demand. My question/concern is with regard to if a building needs a fire pump. Per NFPA 25, annual testing requires the pump be run at 150% of the pump rated capacity. If piping is designed for design fire flow, then maximum allowable velocity will likely be exceeded [at least] annually during the fire pump test.
How do other utilities approach pipe sizing when a fire pump is involved? Without much reference to go on, I've tentatively set a rule for 10 ft/s at design flow or 12 ft/s at pump runout (150%), whichever is more stringent (not everyone needs a fire pump). I'm curious if others feel this is too stringent (should base on design flow only?) or even maybe too lax (10 ft/s max, even at runout?)?
We had to ask someone to make a costly 12-in extension as opposed to an 8-in for a 1500 gpm fire flow, but I wasn't comfortable with an 8-in knowing they would be flowing at 2,250 gpm (14+ ft/s) at least once a year.
Any thoughts?
How do other utilities approach pipe sizing when a fire pump is involved? Without much reference to go on, I've tentatively set a rule for 10 ft/s at design flow or 12 ft/s at pump runout (150%), whichever is more stringent (not everyone needs a fire pump). I'm curious if others feel this is too stringent (should base on design flow only?) or even maybe too lax (10 ft/s max, even at runout?)?
We had to ask someone to make a costly 12-in extension as opposed to an 8-in for a 1500 gpm fire flow, but I wasn't comfortable with an 8-in knowing they would be flowing at 2,250 gpm (14+ ft/s) at least once a year.
Any thoughts?