We are required to design a 11kV system for a rated fault current of 25kA for 1 sec. Based on this requirement the minimum cross section of XLPE insulated Cu cable to be used comes out as 185 sqmm. The actual current required for feeder is 40A.
Now my question:
The permissible short circuit rating of the cable is calculated based on the initial conductor temperature of 90 deg C and final conductor temeperature of 250 deg C. Since the cable is not loaded to its rated current the initial temperature is not going to be 90 deg C as ssumed earlier and hence the actual short circuit handling capacity would be higher than calculated. Is there a method to calculate the actual temperature rise for a particular cross section? Can anyone guide me how to proceed further on this?
Thanks
SKM
Good day gives you happiness, Bad days give you experience. Count Both....
Now my question:
The permissible short circuit rating of the cable is calculated based on the initial conductor temperature of 90 deg C and final conductor temeperature of 250 deg C. Since the cable is not loaded to its rated current the initial temperature is not going to be 90 deg C as ssumed earlier and hence the actual short circuit handling capacity would be higher than calculated. Is there a method to calculate the actual temperature rise for a particular cross section? Can anyone guide me how to proceed further on this?