- Sep 29, 2004
- 46
I am looking for some help.
For HVAC unit I have three Copeland compressors units, which are connected (piped) in tandem. Each compressor rated three phase 460V, 60Hz,load current is 18.6 amp. Each compressor will operate from its own contactor rated for 34 amp equipped with electronic overload relay adjustable range 15-45.
Am I allowed by NEC have only one branch circuit protection circuit breaker for all three compressors? If yes, how to size it? I was reading NEC paragraph 430.53,and got lost.
Thank you,
PaulBr.