mesutphen
Electrical
- Nov 13, 2009
- 35
I have a problem with our 7200V system that I want to fix. Our 7200V system is split into 2 busses. While starting a 10,000 HP Induced Draft (ID) fans, we must shut the tie breaker. If we do not, we will drop our 480V power centers on undervoltage. The problem here is that with the tie breaker shut, the available short circuit current (Isc) is 113kA, and the largest-rated breaker I have been able to find is 77 kA. With the tie breaker open, available Isc is only 56kA.
I’m looking at the solution from 2 perspectives: 1. Find a way to start an ID fan without having to shut the tie breaker, or 2. Find a way to limit the Isc with the tie breaker shut.
For limiting Isc with the tie shut, I have calculated the size of CLR I would need to limit the Isc while starting the fan, and 26MVA is the minimum size. Mainly due to physical size constraints, and also due to the huge cost associated with buying 2 of these, I would rather not go this path.
For starting the fan with the tie open, I have thought that maybe a capacitor bank in parallel with the fan may help, and would be cheaper and smaller than the CLR. However, I am not sure whether shifting the power factor will actually help, and am not sure about being able to switch the bank in and out fast enough to not have a bad effect on the rest of the system (specifically the generator). I know getting a different supply transformer, with a lower impedance, will help, but the cost for this makes me not want to go that path either.
The 7200V busses are supplied from the generator through our Unit Auxiliary Transformer (UAT) which is a 40/20/20MVA, supplying 7200V bus A through X winding at 14.054% impedance, and bus B through Y winding at 14.218% impedance. The 480V power centers are all supplied from the 7200V busses through individual transformers.
Does anyone have any other suggestions to:
a. Minimize voltage drop on the 7200V busses during ID fan starting
OR
b. Limit Isc while the tie breaker is closed
I’m looking at the solution from 2 perspectives: 1. Find a way to start an ID fan without having to shut the tie breaker, or 2. Find a way to limit the Isc with the tie breaker shut.
For limiting Isc with the tie shut, I have calculated the size of CLR I would need to limit the Isc while starting the fan, and 26MVA is the minimum size. Mainly due to physical size constraints, and also due to the huge cost associated with buying 2 of these, I would rather not go this path.
For starting the fan with the tie open, I have thought that maybe a capacitor bank in parallel with the fan may help, and would be cheaper and smaller than the CLR. However, I am not sure whether shifting the power factor will actually help, and am not sure about being able to switch the bank in and out fast enough to not have a bad effect on the rest of the system (specifically the generator). I know getting a different supply transformer, with a lower impedance, will help, but the cost for this makes me not want to go that path either.
The 7200V busses are supplied from the generator through our Unit Auxiliary Transformer (UAT) which is a 40/20/20MVA, supplying 7200V bus A through X winding at 14.054% impedance, and bus B through Y winding at 14.218% impedance. The 480V power centers are all supplied from the 7200V busses through individual transformers.
Does anyone have any other suggestions to:
a. Minimize voltage drop on the 7200V busses during ID fan starting
OR
b. Limit Isc while the tie breaker is closed