RTD input to PLC...

Status
Not open for further replies.

cfordyce

Electrical
Jun 26, 2002
55
If a PLC does not have a special RTD input module, what is the best way to be able to read a RTD input with the PLC? Can an analog voltage or current input card be used with accuracy? Or are there economically feasable devices to convert the signal from the RTD? Any suggestions?

The RTDs are all 100ohm Platinum.

Mmmmmm.
 
Replies continue below

Recommended for you

Use an RTD to 4-20ms converter. For cost effective ones look at Kele. These are not any good for process control but are good for BAS uses. You cannot accurately use RTD to standard input modules for any steady current will cause the temp in the RTD to rise P=I*E. This is one of the draw back of RTD’s.
 
Also look at Inor I have calibrated these in the field and they seem to work quite well. Joecontrol
 
ActionPak , Mighty Module, and RIS (Rochester Instrument System) also make convertors.
 