RPZ Horizontal Installation

Status
Not open for further replies.

texanman

Mechanical
May 21, 2008
37
RPZ requires horizontal installation. Most of the lease finish-outs don't have space allocated for this install. Is above the ceiling acceptable and ok location?
Thanks.
 
Replies continue below

Recommended for you

You are incorrect in stating that an RPZ requires horizontal installation. There are several rated rpz that are allowed to be vertical.

Go to for a list of which backflow protectors are rated for vertical flow.

If the rpz is small(~1" or less), above the ceiling can be worked - I wouldn't do it because you still have to drain the relief so you will have a pipe coming out of the ceiling to the drain
 