JD2
Structural
- Apr 15, 2003
- 46
I have a remodel job (one story building approximately 16,000 sf, original drawings are dated 1971) where the drawings indicate a metal roof deck with a lightweight fill. The Architect is going to locate approximately 9 relatively large skylights as part of the remodel. My concern was the reduction in allowable roof diaphragm capacity. When I went out to the job site for an initial visit, I found the roof deck to be a 2" thick orange fibered board topped with approximately 2-1/2" of a light weight gypsum material topped with a built-up gravel roof. Metal straps were welded to the top chord of the joists at 24"o.c. similar to top chord bridging (I assume this provides a brace point for the top chord of the joist and also helps to support the fiber board - see attached photograph), but I couldn't tell how, or if, the metal straps were attached to the fibered board. I was wondering if anyone had ever used or analyzed a similar system, how it is attached to the metal straps and where I might be able to locate some representative values for diaphragm shear to attempt an analysis. My alternative was to place in plane x-bracing wherever a skylight hole was cut to transfer the amount of force that the cut out area would have resisted. Any ideas or thoughts would be appreciated.