revisit 400A branch on 400A main

Status
Not open for further replies.

cryomark

Electrical
Nov 10, 2000
21
for your reference thread237-122674

I'm re-thinking this installation and wonder about the feasability of the following:

The panel board is squareD I line HCW, with a 400A main.
Square D literature qualifies it as service equipment. The load is a westinghouse combination starter with switch, fuses, contactor and overload feeding 200 HP motor.

Can the feed to the starter draw directly off the panelboard mains, without running through a branch CB? This provision seems to be provided for by availability of Square D sub feed lugs.