I am evaluating a Revamp project.It requires a 4"x P x 6" safety valve.
The inlet line loss is between 12% to 16% of set at actual valve capacity.
The Client says the next opportunity to increase inlet pipe size will be in the year 2030.
The outlet pipe friction slightly exceeds 50$ of set.
The current view is to install a remote sensor Pilot safety valve.
This would in theory be an adequate design both high friction loss on both inlet & outlet pipe.
Calculations show the orifice size is adequate despite the high losses.
One concern is "good engineering practice".
Just because something "can be done" does not mean "it shall be done"
This is a Safety System and one should hesitate before pushing the limits.
In my conventional view - any inlet loss above 10% of set should have the piping redesigned.
Is there a "percent of set" limit for remote sensor pilot design??
Any comments are appreciated
The inlet line loss is between 12% to 16% of set at actual valve capacity.
The Client says the next opportunity to increase inlet pipe size will be in the year 2030.
The outlet pipe friction slightly exceeds 50$ of set.
The current view is to install a remote sensor Pilot safety valve.
This would in theory be an adequate design both high friction loss on both inlet & outlet pipe.
Calculations show the orifice size is adequate despite the high losses.
One concern is "good engineering practice".
Just because something "can be done" does not mean "it shall be done"
This is a Safety System and one should hesitate before pushing the limits.
In my conventional view - any inlet loss above 10% of set should have the piping redesigned.
Is there a "percent of set" limit for remote sensor pilot design??
Any comments are appreciated