jamesbanda
Chemical
- Sep 21, 2004
- 223
The purpsoe of this is to understand peoples conventions on this.. generally it does'nt impact the calcs but on a revalidation i'm doing it is close to needing a new valve.. so i'd like some input please..
So, when you size for the fire case
Q= FA^0.82 : Fire duty = Q/ Latent heat.
Is the latent heat/ temp at
1. Pressure = PSET pressure
2 Pressure = Set pressure + over pressure margin.. (as you approach the critical pressure latent heat really drops off..)
I think it is at 2, because in a fire the vessel will be operating at the pressure = PSET + P over pressure.
(I'd rather it be no 1 as my RV is smaller but think that is not correct..)
So, when you size for the fire case
Q= FA^0.82 : Fire duty = Q/ Latent heat.
Is the latent heat/ temp at
1. Pressure = PSET pressure
2 Pressure = Set pressure + over pressure margin.. (as you approach the critical pressure latent heat really drops off..)
I think it is at 2, because in a fire the vessel will be operating at the pressure = PSET + P over pressure.
(I'd rather it be no 1 as my RV is smaller but think that is not correct..)