Question: Installing power line monitoring equipment

Status
Not open for further replies.

rmore

Electrical
Feb 4, 2011
35
I've read the followiong caution on a few commercial power line monitors.

"Caution: Do not install this ddvice on any outlet that does NOT have at least 10 meters of wire between the electrical outlet and the electrical service panel"

Can someone explain the reasoning behind this caution?
 
Replies continue below

Recommended for you

Probably about prospective short circuit current. Rather unusual, I think. What device is it?

Gunnar Englund
--------------------------------------
Half full - Half empty? I don't mind. It's what in it that counts.
 
Often a requirement when MOVs are present in the device. MOVs require impedance in the supply to prevent their destruction during over-voltage transients.

Keith Cress