digitrex
Electrical
- Mar 29, 2004
- 92
Hello,
I have an offshore installation with an 11kV bus, like this:
- Five 11kV generators connected to the 11kV switchboard, 4nos 2.7MW and 1no 4.2MW, installed at different time.
- All generator neutrals are brought to a switching (contactor) panel so that only one neutral is grounded.
- The NGR at the neutral switching panel is 31.75ohm, limiting ground fault currents to 200A.
Now we have a plan to add 3 more generators. Unfortunately I am coming to a problem with the neutral switching panel because:
- there is no isolation switch to isolate half of the switching panel for extension to add more generator neutrals.
- I need to shutdown all the generators in order to make the neutral switching panel safe for extension, which I need to avoid.
I am considering 2 options to overcome this:
(1) Install a new neutral switching panel so that the existing neutrals can be transferred over to the new panel in stages.
(2) Eliminate all the generator neutral groundings and replace by two nos of earthing transformers that can be used to supply power generator auxiliaries. This means that the 2nos existing delta-star transformers to aux switchboard are to be replace by 2nos zig-zag transformers. The neutral grounding for the 11kV system will be provided by the 2nos zig-zag transformers.
Option (1) is possible.
Option (2) is my idea of avoiding Option (1) in order to avoid searching for new spare spaces for the new switching panel. Moreover, I won't have to worry about how many new generators to be added in the future.
I am not sure whether Option (2) is a good idea and I would like to have your views.
I have an offshore installation with an 11kV bus, like this:
- Five 11kV generators connected to the 11kV switchboard, 4nos 2.7MW and 1no 4.2MW, installed at different time.
- All generator neutrals are brought to a switching (contactor) panel so that only one neutral is grounded.
- The NGR at the neutral switching panel is 31.75ohm, limiting ground fault currents to 200A.
Now we have a plan to add 3 more generators. Unfortunately I am coming to a problem with the neutral switching panel because:
- there is no isolation switch to isolate half of the switching panel for extension to add more generator neutrals.
- I need to shutdown all the generators in order to make the neutral switching panel safe for extension, which I need to avoid.
I am considering 2 options to overcome this:
(1) Install a new neutral switching panel so that the existing neutrals can be transferred over to the new panel in stages.
(2) Eliminate all the generator neutral groundings and replace by two nos of earthing transformers that can be used to supply power generator auxiliaries. This means that the 2nos existing delta-star transformers to aux switchboard are to be replace by 2nos zig-zag transformers. The neutral grounding for the 11kV system will be provided by the 2nos zig-zag transformers.
Option (1) is possible.
Option (2) is my idea of avoiding Option (1) in order to avoid searching for new spare spaces for the new switching panel. Moreover, I won't have to worry about how many new generators to be added in the future.
I am not sure whether Option (2) is a good idea and I would like to have your views.