mls1
Electrical
- Aug 15, 2002
- 133
We have a large hydrogenerator excitation system in which the PPT (power potential transformer) that feeds the exciter is fed from a a fused tap off the generator IPB. The PPT secondary conductors are then fed to the exciter cabinet via cables in tray. The AC breaker they land on has no overcurrent protection. This seems to violate NEC 240.21 on several levels. First, the transformer is delta/wye connected so primary protection cannot be use to protect the secondary conductors. Second, the conductors must be sized to a protective device upon which they terminate but there is no protective device at the termination, and third the conductors must be installed in a raceway but cable tray is a cable support system, not a raceway. Is there something specific to PPT installation that excludes the requirements for transformer secondary conductors in the NEC?