I would request the Forum Members to suggest the type of cables to be used for connecting following I/Os to DCS/PLC based on their experience.
1 Analog inputs 4-20mA (from transmitters & VFD feedbacks)
2 Analog inputs Thermocouples
3 Analog inputs RTDs
4 Analog outputs 4-20mA (to I/P converters & VFD reference)
5 Digital inputs - voltage 24v DC (from field swithches & aux. potetial free contacts in MCC/VFD)
6 Digital outputs voltage 240/110 v AC (commands for start/stop, open/close to MCC/Solenoid coils)
Normally these I/Os are grouped (typewise)in Field Junction/Marshalling boxes so that Multicore/pair cable can be run from field to PLC/DCS panel in the control room.
Can we use Multicore armoured (0.8sq.mm for AI/AOs, 1.5sq.mm for DI/DOs & 1.32sq.mm for thermocouples)?
Or we have to use multipair screened cables for the above applications.
R.Thiyagarajan.
1 Analog inputs 4-20mA (from transmitters & VFD feedbacks)
2 Analog inputs Thermocouples
3 Analog inputs RTDs
4 Analog outputs 4-20mA (to I/P converters & VFD reference)
5 Digital inputs - voltage 24v DC (from field swithches & aux. potetial free contacts in MCC/VFD)
6 Digital outputs voltage 240/110 v AC (commands for start/stop, open/close to MCC/Solenoid coils)
Normally these I/Os are grouped (typewise)in Field Junction/Marshalling boxes so that Multicore/pair cable can be run from field to PLC/DCS panel in the control room.
Can we use Multicore armoured (0.8sq.mm for AI/AOs, 1.5sq.mm for DI/DOs & 1.32sq.mm for thermocouples)?
Or we have to use multipair screened cables for the above applications.
R.Thiyagarajan.