Hello all,

I am designing a sediment basin with a required detention time of 15 hours. I developed my hydrograph and determined the volume and required discharge. I need to know how to calculate the maximum discharge from a pipe of given diameter. The basin is designed to be 3.5 feet deep with the outlet pipe 6 inches of the floor. Consequently, the pipe could have a head pressure of 3 feet. Any help is greatly appreciated.

Scott
 
Replies continue below

Recommended for you

If the pipe is a culvert, open on both ends and relatively short, then use the procedures outline in the FHWA's HDS 5 or the comp prog HY8. If the pipe is connected to a system, ie: storm drain, then use Hydraulic grade computations. In either case you can get a priliminary size based on inlet control and then fine tune from there.

Here is a link to FHWA's website:


if you follow the software link to on that page you can dl HY8.
 
For a quick and dirty maximum flow rate, assume a 6" orifice
(Ok if the pipe is very short, like only the width of a 8" wide concrete block retaining wall). The orifice equation is Q = 0.6*Ao*H^.5, where Ao = pi*.25^2 and H = (3.5-.25) so Q = 0.2 CFS. Of course, if the pipe end is projecting on the inside, the flow will be reduced, and if the inside pipe end has a nice bell, the flow will be increased. The analysis assumed a flat, sharp end. (The constant will change with your units.)
Best of Luck.....

Clifford H Laubstein
FL PE 58662
 
I found this equation. Is this what I'm looking for?

Q=A*sqrt(2gH/1+Ke+KpL)

Where
Q = Flow Rate
g = Acceleration due to graviity 32.2 ft/sec
H = Head on the pipe
Ke = Entrance Loss Coefficient
Kp = Pipe Loss Coefficient
L = Length of Pipe

Ke = 1
Kp= 5087*n^2/d^(4/3)
Where
n = Mannings "n" for selected pipe
d = diameter of pipe

Is this even close to what I need?

Any help is greatly appreciated.

Scott
 

Hello,

That seems to be what you need indeed, with A=section of your outlet pipe and H= 3.5feet minus 6inches minus pipe's diameter.
the constants may be different from what I know (working with meters).
Junction headloss: Ke#1/m2 with m flow coefficent gibfrog was talking about, m equals 0.6 for a standard sharp junction: Ke=1 is for a smoothed junction.
Linear headloss: Kp can be evaluated using colebrook formula (wich needs iterating) or an analog formula.

I hope this answers to you question...

David

 
For culverts, there are pipe flow nomographs availabe. The ones I use I obtained from the Kentucky Higway Drainage Manual. I suspect most state highway departments will have something similar. Your culvert manufacturer should also have something. For a riser, I generally use the a combination of equations for an orifice flow and full pipe flow, taking the minimum of the two solutions.
 