Pile Capacity Quick Help!!!

Status
Not open for further replies.

jgeng

Structural
May 23, 2009
61
I am not a geotech...I need a ball park figure for the capacity of an 8" tip timber pile driven below water into fine sand 6ft. The first 2 ft was reported to be dense fine sand with N=40. After that it is medium dense fine sand with silt with N=20.

What would be a resonable bearing capacity using end bearing alone and then using the skin friction too?

I was given very high numbers that I don't think are right. Are there any rules of thumb for end bearing and skin friction?
 
Replies continue below

Recommended for you

allowable end bearing pressures of a pile are generally much higher than that of a footing due to the constraint of the surrounding soil.
 
I haven't done the calcs, but I would believe you'd be good for at least 25 tons (US). I drove timber piles into a 10 ft sand lens - about half way in and we used 25 tons on the load; no problems. As the material below was a very soft clay we didn't put in pile groups - but placed the piles along grade beams at wide spacings so we had no overlap - had done a pile load test on this to confirm. If you do the calcs use the Nordlund approach for the skin friction - due to the taper of the timber piles you will get some "bearing" along the shaft as well.
 
These piles were likely jetted in, what effect would that have on the capacity?
 
Jetting reduces the skin friction significantly. I have in the past ignored the skin friction component entirely and used the end bearing only.
You may not be able to design for more than 8 or 10 tons out of a pile that is jetted.
 
Your first posts says "driven", then jetted. You should have some way of getting some load into them before use if possible. Even a back-hoe with full bucket has some pretty good hammering effect.

A common way to install docks is by jetting. Can you check out any similar sites where jetting was used and see how the job looks? That jetting will destroy a lot of that density that is now present. It even will mess up the end bearing. 10 tons is plenty then. What's going on top? Can that settle a little?
 