I got a bit confused with some manufacturers application notes stating that no overvoltages occur in systems with neutral grounding resistors...I understand that from phasor diagrams the neutral point will shift during line-to-ground faults, for both low resistance and high resistance grounding....correct me if I am wrong!
It seems that they meant by overvoltages the dangerous transient oscillations due to arcing ground faults, where system inductance and capacitance inter-exchange energy (this happens in IT systems). However, the NGR systems will have a line-to-line voltages appearing on healthy phases to ground.
Any clue?
It seems that they meant by overvoltages the dangerous transient oscillations due to arcing ground faults, where system inductance and capacitance inter-exchange energy (this happens in IT systems). However, the NGR systems will have a line-to-line voltages appearing on healthy phases to ground.
Any clue?