Ipetu
Structural
- Jun 5, 2007
- 54
Please see attached drawings and photo (multi-page PDF).
Existing slab is 10" thick, rebar is #6, f'c = 3000 psi. Rebar pattern in this area seems to suggest that the slab is spanning mainly in the left to right direction. No special rebar is called up around the existing opening. Client wants a new opening as shown. Approx. 20 ft between gridlines.
Using a conservative 60 psi for shear stress in the plain concrete (0.02f'c with f'c = 3000 psi), a 1 ft strip of slab with d = 8.875 in (d = h-cover-bar diameter/2)has V = 60 psi x 12 in x 8.875 in = 6390 lb / ft. Relatively speaking this is fairly high and can support a fair bit of load. So I have ruled out shear as a concern.
Analysing the effect of the proposed opening in flexure is proving to be a challenge. However, considering that the proposed opening seems to fall within a middle strip, I am leaning toward saying that it is acceptable.
Any thoughts, comments etc. appreciated.
Existing slab is 10" thick, rebar is #6, f'c = 3000 psi. Rebar pattern in this area seems to suggest that the slab is spanning mainly in the left to right direction. No special rebar is called up around the existing opening. Client wants a new opening as shown. Approx. 20 ft between gridlines.
Using a conservative 60 psi for shear stress in the plain concrete (0.02f'c with f'c = 3000 psi), a 1 ft strip of slab with d = 8.875 in (d = h-cover-bar diameter/2)has V = 60 psi x 12 in x 8.875 in = 6390 lb / ft. Relatively speaking this is fairly high and can support a fair bit of load. So I have ruled out shear as a concern.
Analysing the effect of the proposed opening in flexure is proving to be a challenge. However, considering that the proposed opening seems to fall within a middle strip, I am leaning toward saying that it is acceptable.
Any thoughts, comments etc. appreciated.