Ciaci
Mechanical
- Jul 11, 2015
- 66
Hi all,
I am designing a total flooding Novec plant. The Same cylinders have to protect multiple hazard volumes. So for the first time I have to design a plant with directional valves. I have to use kidde products because of the client decision.
But there is something in this datasheet that I cannot understand ( ), as it is possible to see in Figure 3, it seems that in order to activate the cylinder are needed 4070 cu. in. driver nitrogen. This is a problem for me beacause of the space issue.
Did someone know if, in this case, it is possible to electrically activate the cylinder without nitrogen drivers?
I tried to contact KIDDE but the italian KIDDE sellers did not answer to my questions.
I hope someone can help me thanks
I am designing a total flooding Novec plant. The Same cylinders have to protect multiple hazard volumes. So for the first time I have to design a plant with directional valves. I have to use kidde products because of the client decision.
But there is something in this datasheet that I cannot understand ( ), as it is possible to see in Figure 3, it seems that in order to activate the cylinder are needed 4070 cu. in. driver nitrogen. This is a problem for me beacause of the space issue.
Did someone know if, in this case, it is possible to electrically activate the cylinder without nitrogen drivers?
I tried to contact KIDDE but the italian KIDDE sellers did not answer to my questions.
I hope someone can help me thanks