AJ2002
Electrical
- Mar 4, 2002
- 27
I need a high speed form A contact (Normally Open commanded closed) be used to drop out a solenoid valve. The form C contact is much slower and millisec's count in the application.
The valve is 125 VDC requires a 180 milliamps to be be held in. Pull-in Voltage: 95-70 vdc & Drop-out 50 to 20 vdc.
If I shunt the solenoid valve with the form A and add a resistor in series with the solenoid valve and shunt contact may work. Any other better ways?
The valve is 125 VDC requires a 180 milliamps to be be held in. Pull-in Voltage: 95-70 vdc & Drop-out 50 to 20 vdc.
If I shunt the solenoid valve with the form A and add a resistor in series with the solenoid valve and shunt contact may work. Any other better ways?