Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations cowski on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Need help on sizing relief valves

Status
Not open for further replies.

ruwl

Petroleum
Jan 26, 2006
12
I am trying to size some PSV's that have properties (hydrocarbons) with MW < 40 and Relief Pressure above 2000 psig. The API curve has a minimum of MW = 40 and a max pressure at 1000 psig.

For Fire case, how do I obtain the Latent Heat of Vaporization and Relief Temperature at the conditions mentioned above?

Can I be conservative and use Latent Heat of 50 btu/# anf relief temperature = (oper. temp./op. press.) x relief pressure?

I would appreciate any suggestion. Thanks.
 
Replies continue below

Recommended for you

It seems to me that when the PSV opens at 2000 psig the contents will be way above it's critical temperature. Therefore, the contents will be a gas and will have NO latent heat of vaporization. So, I'd say you cannot use 50 Btu/lb, because it will not be conservative. Furthermore, the temperature will probably be so high, 500 C or more using ethane as a rough model, you may need to worry about runaway decompostion reactions along with the fire.

Good luck,
Latexman
 
Google "sizing relief valves for supercritical fluids". One hit. I recall that article. I think it was a pretty good one.

Good luck,
Latexman
 
A related thought: this product is probably relieving at above its autoignition temperature. Be sure to pipe the relief line accordingly, and don't aim it at anything that has legal representation or that you want to keep.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor