- Oct 8, 2005
- 32
Does anyone know about the consequences of Motoring of Electric Generator by Breaker failure (Trip Coil was failed and the Generator breaker didn´t open to disconect to the grid).
When the operator unload the machine to shutdown it the control system send the signal to open the generator breaker the trip coil fail and the unit without load and with excitation on the rotor (the field breaker stay still close)the unit get power from the grid and motoring the generator.
The motoring of generator was around five (5) minutes until the operator call to Central Dispatch for clean all bus bar tripped all circuits on the electric substation 69 kV.The operator can´t pull the manual trip on SF6 SIEMENS breaker because he didn´t know how is the procedure to do that.
Our generators are made by BRUSH and the nominal power is 133 MVA and gas turbines are model W501D5 Siemens Westinghouse the nominal capacity is 100 MW ISO conditions
What we do to inspect the generator? What kind of failures are typical when motoring generator? We consulted to Siemens for install a redundant trip coil on SF6 breaker to prevent the same problem on the future.
Regards
Alberto J. Hung C
Caracas Venezuela
When the operator unload the machine to shutdown it the control system send the signal to open the generator breaker the trip coil fail and the unit without load and with excitation on the rotor (the field breaker stay still close)the unit get power from the grid and motoring the generator.
The motoring of generator was around five (5) minutes until the operator call to Central Dispatch for clean all bus bar tripped all circuits on the electric substation 69 kV.The operator can´t pull the manual trip on SF6 SIEMENS breaker because he didn´t know how is the procedure to do that.
Our generators are made by BRUSH and the nominal power is 133 MVA and gas turbines are model W501D5 Siemens Westinghouse the nominal capacity is 100 MW ISO conditions
What we do to inspect the generator? What kind of failures are typical when motoring generator? We consulted to Siemens for install a redundant trip coil on SF6 breaker to prevent the same problem on the future.
Regards
Alberto J. Hung C
Caracas Venezuela