Kasane
Electrical
- Sep 23, 2001
- 3
Can someone advise me the risk/benefits of parallel battery strings.
The requirement is 120V/800AH but we try to standardize on Liberty 1000 series batteries. At one location, the vendor installed a parallel string consisting of two(2)X 40 cell LS3-400 (3vpc)in parallel.
pos--+--C-C-C-C-C-C-C-C-...-C-C-C-C-C-C-C-C-C--+
| |
+--C-C-C-C-C-C-C-C-...-C-C-C-C-C-C-C-C-C--+--- NEG
(40)
The second location consists of 4 cells in parallel with another 4 cells seriesed in 10 segments.
pos--+--C-C-C-C--+---+-C-C-C-C--+
+--C-C-C-C--+ +-C-C-C-C--+--- NEG
(1) (2) ...
I am not familiar with the benefits of the second scenario. Parallel strings are not desirable but the open state failure mode of VRLA batteries has unacceptable consequences.
Terry
The requirement is 120V/800AH but we try to standardize on Liberty 1000 series batteries. At one location, the vendor installed a parallel string consisting of two(2)X 40 cell LS3-400 (3vpc)in parallel.
pos--+--C-C-C-C-C-C-C-C-...-C-C-C-C-C-C-C-C-C--+
| |
+--C-C-C-C-C-C-C-C-...-C-C-C-C-C-C-C-C-C--+--- NEG
(40)
The second location consists of 4 cells in parallel with another 4 cells seriesed in 10 segments.
pos--+--C-C-C-C--+---+-C-C-C-C--+
+--C-C-C-C--+ +-C-C-C-C--+--- NEG
(1) (2) ...
I am not familiar with the benefits of the second scenario. Parallel strings are not desirable but the open state failure mode of VRLA batteries has unacceptable consequences.